干粉灭火器到期了,去进行充装维修好,需要进行什么标识吗?有具体的规范吗

干粉灭火器到期了,去进行充装维修好,需要进行什么标识吗?有具体的规范吗

红门铠甲 | 2024-08-30 13:00
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

磊中 2024-08-30 17:13 00 [回复]举报

根据灭火器维修XF95-2015中6.8.4条款规定每具经维修出厂检验合格的灭火器应加贴维修合格证。维修合格证的内容应包括:a)维修编号b)总质量c)项目负责人签署d)维修日期e)维修机构名称、地址和联系电话等

我头发贼黑 2024-08-31 14:41 10 [回复]举报

嘛意思?维修好了有维修合格证;灭火器维修 XF95-2015第 6.8.4条。拉去维修的话,你这个区域不能拉走超过1/4,建筑灭火器配置验收及检查规范 GB50444-2008第5.1.2条。