消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

未联通疏散通道的阳台能算安全出口吗

办公楼,一层4户如图,大于200平米每套,每套设有2个疏散门,但其中一个通往阳台,这样设计应该不符合规范吧,疏散门应该通往疏散通道,如任意相邻两套合并可满足要求,详见图片。请各位老师帮助解答,谢谢!

南飞野雁 | 2024-07-08 18:11
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

安洪全 2024-07-09 10:24 00 [回复]举报

通往阳台的出口,不能算安全出口。


高山流水2024 2024-07-09 15:55 00 [回复]举报

建筑设计防火规范 GB50016-2014(2018年版) >5.5.9 一、二级耐火等级公共建筑内的安全出口全部直通室外确有困难的防火分区,可利用通向相邻防火分区的甲级防火门作为安全出口,但应符合下列要求:
    1 利用通向相邻防火分区的甲级防火门作为安全出口时,应采用防火墙与相邻防火分区进行分隔;
    2 建筑面积大于1000m²的防火分区,直通室外的安全出口不应少于2个;建筑面积不大于1000m²的防火分区,直通室外的安全出口不应少于1个;
    3 该防火分区通向相邻防火分区的疏散净宽度不应大于其按本规范第5.5.21条规定计算所需疏散总净宽度的30%,建筑各层直通室外的安全出口总净宽度不应小于按照本规范第5.5.21条规定计算所需疏散总净宽度。


根据以上,个人理解:阳台互通,是相互借用了相邻防火分区作为安全出口,且阳台的设计更有利于防烟。需要注意的是疏散净宽度和疏散距离要满足要求。

南飞野雁   回复: 高山流水20242024-07-09 18:24

谢谢您的回答,两个房间是同一防火分区,不是同一户,门正常是上锁的,这样可以吗

0    0 [回复]举报

高山流水2024   回复: 南飞野雁2024-07-12 16:08

当然不能上锁

0    0 [回复]举报

phone0224 2024-07-10 09:23 10 [回复]举报

根据帖主的图所示,可以尝试在虚线墙上开门,至少保证图纸层面是没问题的。如果应要划分为四个套房,套房间不能互通,这个是不可以的。阳台不能算安全出口的。

南明离火 2024-07-10 16:07 10 [回复]举报

不能算  相当于房间嵌套了

关闭

关闭

手机APP下载