消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防水带的燃烧性能

消防水带规范上未找打消防水带的燃烧性能及火灾危险性划分,请教下:存放消防水带的库房应按什么类别划分,那本规范有该问题的相关描述?

夜雨孤枫 | 2024-06-06 11:52
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 4

小女子 2024-06-06 15:28 00 [回复]举报

让甲方给你提供检验报告啊,咱肉眼又看不出来它的燃烧性能,甲方要是没有报告就按可燃固体丙类库房来呗,从严原则。

倜圳 2024-06-07 15:50 00 [回复]举报

丙类

消防网友39206 2024-06-09 16:54 00 [回复]举报

水带由织物层和内衬胶构成,属于可燃固体,因此按照《建筑设计防火规范》GB50016-2014(2018年版)第3.1条 火灾危险性分类的相关规定,应属于丙类库房。

潘天坤 2024-06-16 11:12 00 [回复]举报

楼上几位老师解答的挺详细的

火灾危险性类别按照建规要求来,需要项目提供一些证明资料来证明属于什么样的性质,无法证明可以从严判定。

关闭

关闭

手机APP下载