消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

同一建筑内的不同使用功能区域之间应进行防火分隔应该如何理解?

一个2000平方左右厂房,现被房东分开出租了,出租后1000平方和500平方左右分别是两个丁戊类的金属制品生产车间,还有500平方左右被作为了饮料的储存仓库,这三者之间现在是用彩钢瓦进行相互隔开的,分隔后疏散出口和防排烟是符合的,这样分隔是否符合要求呢?

消防网友31650 | 2024-06-02 21:52
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

我头发贼黑 2024-06-03 08:44 01 [回复]举报

厂房是厂房,仓库是仓库,厂房内只允许设置中间仓库,整体平面布置就不允许

消防网友31650   回复: 我头发贼黑2024-06-11 20:27

谢谢

0    0 [回复]举报

phone0224 2024-06-03 09:38 00 [回复]举报

建议楼主先用防火墙把仓库区和厂房区分隔,然后根据《建规》3.4.1的注2、3、6,研判一下是否能按两栋建筑考虑,防火间距不限。若可以,那所有的消防设计都按两幢建筑做。

消防网友31650   回复: phone02242024-06-11 20:27

谢谢答疑

0    0 [回复]举报

南明离火 2024-06-03 11:37 10 [回复]举报

只有中间仓库的概念,没有 厂房里面设仓库的说法

消防网友31650   回复: 南明离火2024-06-11 20:28

谢谢

0    0 [回复]举报

关闭

关闭

手机APP下载