关于大型商业综合体内餐饮商铺的疏散门设置问题

商铺面积超过120平,设置了两个疏散门;

但商铺设计时,一个疏散门在厨房内,厨房面积超过50平;

请问,商铺需要在就餐区再增设一个疏散门吗,就餐区人员可以借用厨房疏散门疏散吗

Gesk.Des | 2024-02-01 17:24
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

安洪全 2024-02-02 09:03 10 [回复]举报

建筑防火通用规范 GB55037-2022

7.4.2 公共建筑内每个房间的疏散门不应少于2个

这个商铺有了两个疏散门,疏散总宽度够,分布间距够,满足疏散距离就可以。

消防网友62117 2024-02-02 11:43 00 [回复]举报

GANSTER 2024-02-18 11:14 00 [回复]举报

就餐人员不可以借用厨房疏散。疏散路径应该是:房间--走道--安全出口

飞翔的心 2024-02-18 14:14 00 [回复]举报

就餐区人员不应借用厨房的疏散出口,先按面积计算需要的安全出口数量。