消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

稳压泵启泵后触发喷淋泵动作

最近遇到湿式自动喷水灭火系统个奇怪的事情,持续到现在已有4周了,大约每5天一个周期,首先是稳压泵启泵补压,7秒钟后延迟器上方的压力开关启动喷淋泵,4秒钟后稳压泵停泵,7秒钟后压力开关回答撤销。系统管网外部检查(含末端放水)未发现泄漏情况。个人认为是个不正常的情况。求大神指点!

卡卡阿卡 | 2024-01-19 15:58
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 10

陈晓茂 2024-01-20 05:30 00 [回复]举报

你检查一下湿式报警阀的微动补水装置的止回阀,是不是卡死了。

红色ID 2024-01-20 22:38 00 [回复]举报

把湿式报警阀上端压力打高一点儿,再就是湿式报警阀下端供水压力设置到合适的范围...

好好干 2024-01-21 00:55 00 [回复]举报

首先你的系统肯定有微微渗漏(或者有人在用消防水),其次你的稳压泵电接点压力表的启停值设置可能有问题

BOLIN 2024-01-22 09:35 10 [回复]举报

这种情况我也遇到过 当时搞检测在屋顶启稳压泵结果报警阀压力开关动作连锁启泵 把水泵法兰阀瓣给打出来了。我们检测都很正常,唯一怀疑的是稳压泵扬程大导致的!

南明离火   回复: BOLIN2024-01-22 10:45

有没有可能是延迟器堵头堵了

1    0 [回复]举报

BOLIN   回复: 南明离火2024-01-22 14:29

我们搞过现场压力开关连锁启泵 正常的

0    0 [回复]举报

任重道远 2024-01-22 09:37 00 [回复]举报

稳压泵的公称流量应小于系统自动启动流量。

在临时高压消防给水系统中,稳压泵设计流量应小于系统自动启动流量,但对于自动喷水灭火系统,宜予区别对待。

(1)稳压泵设计流量应小于系统自动启动流量,在设置稳压泵组的临时高压给水系统中,当通过消防水泵出水干管上的压力开关直接自动启动消防水泵时,稳压泵设计流量应小于系统自动启动流量,方可满足“消防水泵出水干管压力开关连锁启动消防水泵”的控制要求。

(2)闭式自动喷水灭火系统难以适应该规定要求。不同于室内消火栓等消防水灭火设施,自动喷水灭火系统主要依靠其报警阀组的压力开关连锁启动消防水泵,如按本条文规定要求确定稳压泵流量,则可能导致报警阀组不能有效动作,贻误灭火时机。


可能是系统存在泄漏,该泄漏值已达最小系统启动流量且稳压泵设定启动值低于报警阀组的启动设定值。

其次在考虑组件及电气元器件的问题。

南明离火 2024-01-22 10:42 00 [回复]举报

这么有规律 ,是不是阿姨一段时间 开个试水阀 拖地,用完关掉

牛疼 2024-01-22 13:35 00 [回复]举报

1、不排除有系统内的阀门存在泄露的可能,例如:泄压阀、应急泵止回阀等;

2、有规律的频繁出现此类现象,有可能是主机、泵控柜等电箱自带的巡检功能;

3、有规律的频繁出现此类现象,极有可能是有人定时使用消防水;

4、冬季,可能是有的地方冻住了,导致的个别组件无法正常使用了。

阿龙 2024-01-23 08:34 00 [回复]举报

应该是上下腔之间补偿器堵了,一点点水流波动就会冲开阀瓣导致压力开关动作,如果补偿器正常的话就不会出现这种情况。

关闭

关闭

手机APP下载