同一防烟分区内设置两种不同的排烟方式

假设走道净高3米,两侧自然排烟窗1.5米以上开启有效排烟面积无法满足要求的情况下增设机械排烟 ,两侧自然排烟窗是否需要改成固定窗,如果不改是否会影响机械排烟的排烟效率。

WeiHL | 2023-11-09 16:14
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

阳明心 2023-11-09 16:37 00 [回复]举报

根据《消防设施通用规范》GB 55036-2022

11.3.1 同一个防烟分区应采用同一种排烟方式


所以有必要把自然排烟窗改成固定窗。


周家斌 2023-11-10 09:09 00 [回复]举报

可以在储烟仓以下设置开启窗,也便于日常通风换气用,还有利于排烟时补风。

郝琦   回复: 周家斌2024-03-16 22:44

完美

0    0 [回复]举报

潘天坤 2024-06-19 22:21 00 [回复]举报

机械排烟量如果满足排烟要求即可

同一防烟分区不允许使用两种排烟方式主要担心两种方式结合排烟,导致两种方式相互之间对气流的干扰,影响排烟效果

如果机械排烟量已经满足要求了,那么只要机械排烟工作就行,用不上自然排烟了