三层的小商铺型商业建筑疏散走道宽度

三层的小商铺型商业建筑,每间商铺均与敞开式外廊连通,敞开式外廊的最小宽度是否可以按新发的防火通用规范7.1.4条规定,按1.1米设置?

如不可,那外廊最小宽度按多少执行?


乐先生 | 2023-06-27 23:42
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

同同不同 2023-06-28 06:07 00 [回复]举报

应满足不小于1.1m的要求,尚行根据人数计算疏散宽度,两者取大值

风无心 2023-06-28 20:50 00 [回复]举报

按《民通规》公共走廊净宽最小是1.30m,再根据疏散宽度计算,两者对比取其大者。

张牙舞爪的张 2023-06-29 08:59 00 [回复]举报

三层人员密度按0.56,算出最大人员数量;再根据百人疏散宽度0.75米/百人,且不低于最小疏散宽度1.1米,得出疏散宽度。