消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防救援窗

请问消防泵房需要设置消防救援窗吗?

南瓜1 | 2023-05-19 07:58
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

消防网友78337 2023-05-19 09:04 00 [回复]举报

建筑防火通用规范 GB55037-2022

2.2.3 除有特殊要求的建筑和甲类厂房可不设置消防救援口外,在建筑的外墙上应设置便于消防救援人员出入的消防救援口,并应符合下列规定:     1 沿外墙的每个防火分区在对应消防救援操作面范围内设置的消防救援口不应少于2个;     2 无外窗的建筑应每层设置消防救援口,有外窗的建筑应自第三层起每层设置消防救援口;     3 消防救援口的净高度和净宽度均不应小于1.0m,当利用门时,净宽度不应小于0.8m;     4 消防救援口应易于从室内和室外打开或破拆,采用玻璃窗时,应选用安全玻璃;     5 消防救援口应设置可在室内和室外识别的永久性明显标志。


消防救援窗开设的目的在于在实际火灾事故中,方便消防救援人员直接接近火源,有效灭火。


从通则来看消防泵房非必须要设置消防救援口的场所,

如果地上层消防泵房同层其它公共区域均不法设置外窗,消防泵房内设置消防救援口也是可以的.


南明离火 2023-05-19 10:37 00 [回复]举报

消防泵房正常都有直通室外的门,可以作为救援门使用,也没必要局限于窗这个概念吧

明亮晶莹 2023-05-19 15:52 00 [回复]举报

没有规定必须设

永锅 2023-05-23 10:06 00 [回复]举报

不需要。

风无心 2023-06-17 23:54 00 [回复]举报

这个是不需要的,救援谁呢?人都没有。

马先森627 2024-04-01 16:30 00 [回复]举报

按照某些审图老灯的意见,规范没说不可以,就必须设。

关闭

关闭

手机APP下载