消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

有个高层办公楼,1-5层是商业用途,三层有个餐厅(原主体设计就是做餐厅),但是对于他疏散宽度的计算方式我不太了解,不知有没有大神能帮我解答下

小马 | 2020-11-30 16:53
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

小马 2020-11-30 17:23 30 [回复]举报

第一个就是人员数量的确定,根据办公室规范里面消防设计一章,办公人数无法确定时不时按9m2一个人计算,他这个12怎么来的,然后其他几个人数与平方比出自哪里?

第二个疏散人数的换算系数,一二层取0.85,三层取0.77,四层取0.6是出自哪里?

小弟搜了好久都没找到答案

黄辉 2020-12-01 10:25 00 [回复]举报

办公室人员面积参考:办公建筑设计标准 JGJ/T67-2019   4.2节


4.2.3 普通办公室应符合下列规定:
    1 宜设计成单间式办公室、单元式办公室、开放式办公室或半开放式办公室;
    2 开放式和半开放式办公室在布置吊顶上的通风口、照明、防火设施等时,宜为自行分隔或装修创造条件,有条件的工程宜设计成模块式吊顶;
    3 带有独立卫生间的办公室,其卫生间宜直接对外通风采光。条件不允许时,应采取机械通风措施;
    4 机要部门办公室应相对集中,与其他部门宜适当分隔;
    5 值班办公室可根据使用需要设置,设有夜间值班室时,宜设专用卫生间;
    6 普通办公室每人使用面积不应小于6m²,单间办公室使用面积不宜小于10m²。
4.2.4专用办公室应符合下列规定:
    1 手工绘图室宜采用开放式或半开放式办公室空间,并用灵活隔断、家具等进行分隔;研究工作室(不含实验室)宜采用单间式;自然科学研究工作室宜靠近相关的实验室。
    2 手工绘图室,每人使用面积不应小于6m²;研究工作室每人使用面积不应小于7m²。


规范用词室不应(或不宜)小于,设计师可以根据办公室档次,确定每人使用面积。

小马   回复: 消防网友52182020-12-03 17:36

您截给我的这个规范的第五章 5.0.3 办公建筑疏散总净宽度应按总人数计算,当无法额定总人数时,可按其建筑面积9m²/人计算。

不知设计时候可以按照9m2来计算疏散宽度

0    0 [回复]举报

PQ 2020-12-02 10:24 70 [回复]举报

1、人员密度一般可查询相应专项规范(该项目可能依据已作废的老版本),但应注意一些建筑专项标准所规定的人数指标或人均使用面积指标,仅供参考和比对,并非实际的使用人数或疏散人数。疏散人数应为建筑使用期间任何时间内的可能最大人数。在确定相应建筑的疏散人数时,还应根据当地相同建筑中类似用途场所的实际使用情况经调查确定,不能简单地按照这些标准规定的指标来计算。

2、换算系数是按照建规06版5.3.17规定来的:

小马   回复: 消防网友52182020-12-03 17:34

谢谢大神答疑解惑,其实我主要就是对他取的这几个系数不知道哪来的,但是这个项目是新项目,不知为何设计时候还是采用已经废止的规范来进行,

0    0 [回复]举报

关闭

关闭

手机APP下载