8层医疗病房楼,按照消防规范要求设置了消火栓和自动灭火系统。请高手回答,某层末端试水装置压力显示0.30MPa,是否合理?

消防网友62482 | 2023-04-15 08:42
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

286914067@qq.com 2023-04-15 13:55 00 [回复]举报

是动压还是静压!

消防网友78337 2023-04-15 15:35 00 [回复]举报

消防给水及消火栓系统技术规范 GB50974-2014 

6.2.1 符合下列条件时,消防给水系统应分区供水:     1 系统工作压力大于2.40MPa;     2 消火栓栓口处静压大于1.0MPa;      3 自动水灭火系统报警阀处的工作压力大于1.60MPa或喷头处的工作压力大于1.20MPa。

自动喷水灭火系统设计规范 GB50084-2017 

5.0.1 民用建筑和厂房采用湿式系统时的设计基本参数不应低于表5.0.1的规定。

注:系统最不利点处洒水喷头的工作压力不应低于0.05MPa。


一路同行 2023-04-15 16:26 00 [回复]举报

当设置稳压泵时末端压力不低于0.15Mpa

消防老胡 2023-04-15 18:51 00 [回复]举报

合理。依据《消防给水及消火栓系统技术规范 》(GB50974-2014)第5.2.2条“高位消防水箱的设置位置应高于其所服务的水灭火设施,且最低有效水位应满足水灭火设施最不利点处的静水压力,并应按下列规定确定:…… 4 自动喷水灭火系统等自动水灭火系统应根据喷头灭火需求压力确定,但最小不应小于0.10MPa;5 当高位消防水箱不能满足本条第1款~第4 款的静压要求时,应设稳压泵”和第5.3.3条“稳压泵的设计压力应符合下列要求: 2 稳压泵的设计压力应保持系统自动启泵压力设置点处的压力在准工作状态时大于系统设置自动启泵压力值,且增加值宜为0.07MPa~0.10MPa;3 稳压泵的设计压力应保持系统最不利点处水灭火设施在准工作状态时的静水压力应大于0.15MPa”之规定。结论:设了高位水箱,末端≥0.1mpa;设了稳压泵,末端≥0.15mpa。


消防黄河 2023-04-16 12:14 00 [回复]举报

合理