消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

排烟垂直风管和每层水平风管交接处的水平管段上的防火阀距垂直风管所在的风道墙体距离是否也需要小于200MM?

排烟垂直风管和每层水平风管交接处的水平管段上的防火阀距垂直风管所在的风道墙体外皮距离是否也需要小于200MM?    是否水平风管需要满足建规6.3.5  所述风管穿越防火隔墙时,防火阀两侧各2米范围内风管应采用耐火风管?   


wenhua | 2022-11-19 21:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

张牙舞爪的张 2022-11-21 09:46 00 [回复]举报

1、200mm距离只对水平墙体的烟口安装间距做要求。

2、个人理解:垂直排烟管道井壁耐火极限要求不低于一小,已到达防排烟管道中耐火极限要求最高级别。因此不需要。

刘丽波 2022-11-22 23:30 00 [回复]举报

防火分区隔墙两侧防火阀、排烟防火阀才需要小于200mm,其余没有要求。

南明离火 2022-12-01 14:24 00 [回复]举报

潘天坤 2024-07-01 13:39 00 [回复]举报

所有防火阀均要保证距墙大于200毫米要求,规范描述的不是很完整,但是一般都认为所有区域均不应违反

此位置为风管穿越防火隔墙防火阀前后两米区域,需要保证管道防火保护措施


关闭

关闭

手机APP下载