排烟口的最小风速有没有要求?


消防网友73154 | 2022-02-21 15:40
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

消防网友49953 2022-02-22 08:38 00 [回复]举报

最大不要超10,最小风速只要满足要求的排烟量的要求就行

南乡子 2022-02-22 09:20 00 [回复]举报

建筑防烟排烟系统技术标准 GB51251-2017 > 4.4.12 节:排烟口的风速不宜大于10m/s。

中国制造 2022-02-23 13:08 00 [回复]举报

风速大排烟效果好,但太大有缺陷,于是限制了最大风速。你问最小风速,是不是你现场的风速太小?当初设计的时候,设计人员会把风口风速根据不大于10拆分,通常都是很大,因为风速越大风口越少,造价越少,当然也考虑到防烟分区。如果你的风速太小,一定是哪里出了问题。比如:如果每个风口都很小,那就是风机出风口是不是堵了,风管是不是漏风,管内的风阀是不是锈蚀自动关闭了,风机扇叶是不是有断掉的等等。