我晓得2个烟感可以

消防网友49031 | 2022-01-15 22:04
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

大狗狗7 2022-01-17 08:55 00 [回复]举报

不可以,联动启泵的必要条件是。  消火栓报警按钮+一个烟感/一个手报(消规) ;    消火栓报警按钮+2个独立的报警信号(自规)

消防网友34346 2022-01-18 15:43 00 [回复]举报

沐浴阳光 2022-02-09 16:54 00 [回复]举报

    不行。消火栓系统联动控制应由消火栓按钮的动作信号与该消火栓按钮所在报警区域内的任两只火灾探测器的报警信号或任一只火灾探测器和手动火灾报警按钮的报警信号联动控制。GB50166-2019

郭子123 2022-02-11 15:25 00 [回复]举报

不行,启泵必须有消报的参与才可以