面积足够的话,中庭位置不做挡烟措施,上下层可以作为一个防烟分区吗?

面积足够的话,中庭位置不做挡烟措施,上下层可以作为一个防烟分区吗?

漂移 | 2021-09-30 08:10
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

消防网友76443 2021-09-30 15:11 00 [回复]举报

上、下层之间应是两个不同防烟分区,烟气应该在着火层及时排出,否则容易引导烟气向上层蔓延的混乱情况,给人员疏散和扑救都带来不利。在敞开楼梯和自动扶梯穿越楼板的开口部位应设置挡烟垂壁或卷帘,以阻挡烟气向上层蔓延。不得叠加计算防烟分区。

杨江峰 2021-09-30 15:56 00 [回复]举报

面积够,但是不做挡烟不是飘到其他楼层了吗

一片冰雨 2021-09-30 23:45 00 [回复]举报

中庭周边有走廊吗?还是就是一个封闭空间?有走廊的话,走廊与中庭有没有防火卷帘?还有中庭高度是多少?假设它没有走廊是一个封闭的中庭,高度大于9米,可以不设置挡烟措施的,其实你可以把它算做一个独立的大房间的,否则的话,中庭周边的房间、走道怎么处理?