3楼以下的游戏厅,一个厅的疏散也得按照袋型的11.25米来算厅内的任何一点到疏散门的距离么?

3楼以下的游戏厅,一个厅的疏散也得按照歌舞娱乐袋型距(11.25米)来算厅内的任何一点到疏散门的距离么?

距离这个项目在3楼,整个项目就一个大厅, 其他为辅助房间,那么这个大厅内的任意一点到最近疏散门的距离均不能超过11.25米?

消防网友3424 | 2025-03-22 09:33
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

EHS专家-DL 2025-03-24 12:09 00 [回复]举报

厅内任一点到最近疏散门的直线距离≤11.25米(前提:设置自动喷水灭火系统)‌。若未设置自动喷水灭火系统,则疏散距离需≤9米‌。例外情况‌:若大厅通过多个疏散门形成环形疏散路径(如两个疏散门位于不同方向),则可不按袋形走道要求执行,疏散距离可放宽至25米(符合双向疏散条件)‌。

小唐12321   回复: EHS专家-DL2025-03-24 15:06

例外情况哪个规范还是地方标准

0    0 [回复]举报

EHS专家-DL   回复: 小唐123212025-03-25 12:10

建筑设计防火规范 GB50016-2014(2018年版)5.5..


0    0 [回复]举报

LHH2737 2025-03-24 15:14 10 [回复]举报

闲淡潮人   回复: LHH27372025-03-25 10:07

赞同,补充一点需注意该厅的所有出口都为安全出口的前提下,才可采取18m的距离。

0    0 [回复]举报

消防网友3424   回复: LHH27372025-03-27 11:13

才知道有这个文件, 广西这边的图审老师,一直卡9米这个距离, 