悬挂干粉算不算自动灭火设施,可否用于厂房生产部位

悬挂干粉算不算自动灭火设施,可否用于厂房生产部位

T1010 | 2024-12-19 23:11
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

我头发贼黑 2024-12-20 14:40 00 [回复]举报

不算自动灭火设施,当成灭火器还可以

云中飞翔 2024-12-20 20:23 00 [回复]举报

悬挂干粉属于预制灭火设施,一般都配套带有火灾自动探测装置,属于灭火系统的一种。

jinyanwu 2024-12-20 21:49 00 [回复]举报

个人意见,仅供参考:

应该属于一种小型的预制灭火系统。也算一种自动灭火设施吧。不过一般不用于厂房生产部位,主要用于电缆隧道;电缆夹层;计算机房;发电机房;档案室(库房);配电室;地下液压站;通讯机站等工业和民用建筑消防。

梅有名 2024-12-23 15:33 00 [回复]举报

消防设施通规第九章,明确说明,自动灭火要具有自动控制、手动控制和机械应急操作的启动方式,显然悬挂干粉的控制方式是不符合的,所以不能算自动灭火设施。