tx3212输入输出模块,调自动就一直输入反馈

排烟风机控制柜tx3212输入输出模块,一直输入反馈,控制柜调手动输入反馈不亮,调自动就输入反馈亮。是什么情况?

AINI | 2024-12-11 18:30
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

高山流水2024 2024-12-13 16:38 00 [回复]举报

应该是自动控制回路的线接错了,排除设备本身的故障,可能是常开接成常闭了,或者常开触头没有弹开。

EHS专家-DL 2025-03-24 15:01 00 [回复]举报

1、模块质量问题,如模块终端电阻未正确并联(终端电阻要求为10kΩ)‌;

2、接线错误;

3、模块与消防主机的协议不匹配,通信问题导致误报。